Is this the correct way for a European 3 phase Open EVSE?

Hello all;


I'm about to purchase a few OpenEVSE's to install chargers at home, at work and build a mobile one like the Fivari charger. I believe I've looked at everything available online for research, however there's no one source to show how a 3 phase, Euro spec OpenEVSE could be done. Some people have done it but nothing is absolutely clear. In order to not lose any functionality I came up with this, what I believe would be the true way of wiring an open evse with a 3 phase power network.


Some notes;


- Using the AC Relay to power the 4 pole European contactor with 220VAC coil. I don't think there are any contactors with this much power handling, using 12V DC coils. I hope this is the correct way to wire.

- Using the OpenEVSE built in GFCI for GroundCheck success and also using an external RCD to protect for all three phases.

- To see energy consumption in the LCD, I am putting only a single phase through the current measuring CT, this will only show amperage per phase.

- AC test's both (L3-L2) goes to exit of contactor so it would sense 220V AC on both test terminals (in ref. to ground of OpenEVSE board, otherwise 400VAC between both phases, I don't know how it is done) and auto sense Level 2. I hope I am correct with this logic.


Besides the wiring, for this to function properly I believe I need to do firmware modification such that;


- Level 2 nominal voltage for energy calculation should be 220V instead of 240. Also I need to multiply measured L3 current through CT by 3. (for 3 phases)

- To plug the mobile version to single phase 220V schuko, I'll connect only L3 and leave L1-L2 empty. That won't change a thing on the functionality side as EVSE doesn't tell between a single or three phase but in terms of measuring it shouldn't be multiplied by 3. So, I am thinking because this will be Level 1 charging, Level 1 energy calc. formula shouldn't be x3 measured current. It would be great if I could change the names from Level 1, Level 2 to "Single Phase", "Three Phase"

- I also would like to change the language of the LCD menu.


Do these make sense? Is this the correct way to wire? Could anyone direct me towards some links to edit the firmware properly? (I don't know much programming)


Thanks in advance for your help.


Wiring looks good. Only change would be to remove GFCI coil. It is not needed when a RCD is used. The ground check is done with AC_Test lines.


1 person likes this

One more change. The relay coil should be connected directly to both AC_Relay terminals on the OpenEVSE. No external connections are necessary as N and L1 will be switched through the AC_Input connection.


1 person likes this
Thank you for replying. How will the ground check work? Would it work connected as in the diagram I posted originally? As I've said I'm thinking of connecting both AC test to hot wire downstreams for auto detect L2 charging as if they were two 120V hotwires in a 240 setup. Any idea on where to start the language change, changing L1 name to single phase and L2 name to three phase and according energy, power calculations? Thanks!

Ground works by confirming at least one of the test lines has AC flowing from AC_test to ground. You could use the L1 and L2 detection as P1 and P3. 


To change the Language edit strings.cpp here is a small example:


#if defined(BTN_MENU) || defined(SHOW_DISABLED_TESTS) 

const char g_psSettings[] PROGMEM = "Settings";

const char g_psSetup[] PROGMEM = "Setup";

const char g_psSvcLevel[] PROGMEM = "Service Level";

const char g_psMaxCurrent[] PROGMEM = "Max Current";

const char g_psDiodeCheck[] PROGMEM = "Diode Check";

const char g_psVentReqChk[] PROGMEM = "Vent Req'd Check";

#ifdef RGBLCD

const char g_psBklType[] PROGMEM = "Backlight Type";

#endif

#ifdef ADVPWR

const char g_psGndChk[] PROGMEM = "Ground Check";

const char g_psRlyChk[] PROGMEM = "Stuck Relay Chk";

#endif // ADVPWR

#ifdef GFI_SELFTEST

const char g_psGfiTest[] PROGMEM = "GFI Self Test";