I have a question regarding the use RCD type Bs and residual current detectors.
From what i have read online, it seems that EVSE stations require some sort of protection against DC fault currents. This can either be implemented with a type B rcd or a circuit that detects DC currents of 6mA or higher. From what i have read this requirement is stated in the IEC 61851 standard.
Could an expert on this topic perhaps help me clarify if this is also a requirement for single phase AC chargers or just 3 phase AC chargers? Is this an international requirement or just in the EU? I do not have access to these standards and would rather get an answer from someone with experiance on this topic anyways.
Thank you for your time.
1 Comment
OpenEVSE Support
said
7 months ago
DC residual current protection is required in the EU for both single and 3 phase.
Aleš Kramžar
Greatings!
I have a question regarding the use RCD type Bs and residual current detectors.
From what i have read online, it seems that EVSE stations require some sort of protection against DC fault currents. This can either be implemented with a type B rcd or a circuit that detects DC currents of 6mA or higher. From what i have read this requirement is stated in the IEC 61851 standard.
Could an expert on this topic perhaps help me clarify if this is also a requirement for single phase AC chargers or just 3 phase AC chargers? Is this an international requirement or just in the EU? I do not have access to these standards and would rather get an answer from someone with experiance on this topic anyways.