Ventilation

I've noticed that when charging my Tesla on my 40A OpenEVSE, after a while the EVSE limits the charge rate to 20A because it has gotten over 60C.  It stays at 20A for 5 minutes or so, then goes back to 40A for 10 minutes, then back to 20A. Up and down.


I don't think this is a problem, but it does mean that the car charges a little more slowly than it could, since it averages 33A while in this mode.


However, I notice that the OpenEVSE case is a sealed enclosure.  Given that my unit is mounted inside my garage, far from any door or window and not going to get wet, would it be useful to cut some ventilation holes in it for cooling?  I'd probably put them on the side, one near the bottom and one near the top.


Does anyone see any issues with this?


Oh, it's also worth mentioning that the 33A average is at current temperatures (springtime).  In the summer when the garage is hotter, I expect the reductions to be longer and more frequent, and the net charging rate slower.

Shawn we would recommend inspecting your station, you should only see throttling at 40A if ambient temperatures are above 110°F. Please look at the interface between your cables and contactor, this is the most common cause of excess heat. For the Packard contactor with screw terminals, sleeve ferrules must be installed on the cable ends.


Ventilation is not recommended and can be very unsafe. In a sealed enclosure a fire would almost instantly consume all the oxygen go out and the station would shutdown. With ventilation a fire can ignite, continue to burn and spread.

Hmm. My kit came without the lugs, so I cut the ferrules off, stripped the wires and wrapped the wires around the screws. Everything should have really good contact.


I'll let it warm up and then disconnect and open it up and see where the hot spots are.


The argument against ventilation makes sense.

It's the relay (Struthers & Dunn) that's getting hot. The hottest parts of it are the low-voltage screws, which seems odd.  My infrared thermometer measured them at about 160F right after I opened the cover. The input and output terminals were all about 145F.

The low voltage screws power the relay coil. The coil resistance is 70 Ohms so at 12v that is 2.05 watts, so the heat is not too odd.


We will send you heavy duty ring terminals and see if that helps.

Thanks!  Could you also send new wires?  I cut the ends off of mine.  Do you need an address?

I live in Scottsdale AZ and I'm seeing throttling down from 24A to 12A due to high temps.  I've gotten into the habit of directing a room fan at it while it runs.  It seems to do the trick.  I would prefer some sort of beefier built-in cooling option for the EVSE though.

Ken, 


We would recommend inspecting your station, especially the connections between your AC and EV cable and the relay. You should not see throttling at 24A even when it is hot outside.


What version of firmware are you running? We recommend 3.11.3 at a minimum. The early releases of temperature monitoring were ultra conservative. 



I finally got around to updating my firmware yesterday to the latest version - 5.0.1.  I plugged my car in last night and came out to a red-backlit display that indicated the unit had gone over temp.


While I had the unit open, I put ferrules on the high-current feeds in and out of the relay, so I'd say I've eliminated that possibility.  Ambient temp in the garage was around 98F when I started charging.  It would appear that I have one of the displays that is overheating, but I don't have an IR camera to check.


My workaround will have to continue to be directing a fan at it, as that's what I've been doing up to this point.

Hi Ken,


Do you have WiFi sending data to data.openevse.com? If so it is very easy to diagnose the issue. If you have a LCD that has been damaged by Electrostatic Discharge and is running hot, your station will be way over the ambient temperature even at idle. A normal station will run about 2.5°C over the ambient temperature.


Chris

Wondering if this thread is still active?

I've had heat/shutdown issues since charging my new Leaf SV+.  I've changed a bad spade connector and throttled back to 24 amps, but still have issues with the unit shutting down during a long charge.  At 22 amps, the unit gets up to about 110-115 oF at the front surface below the LCD screen.  The "menu" button gets quite hot.  The latest internal issue was a blown fuse with obvious heat damage around the upper terminal of the "white" wiring terminal block - along with an obvious burn smell inside the unit.  

Do you have any suggestions - I've replace the fuse, ensured good connections and taken the IR temps given above.

Mark